Старый 24.11.2016, 18:26   #23
LordN
Senior Member
 
Регистрация: Dec 2007
Адрес: Томск
Сообщения: 4 125
Благодарил(а): 239 раз(а)
Поблагодарили: 161 раз(а) в 153 сообщениях
По умолчанию Ответ: Honeywell MVC80-DH10M

забыл, вот логи обмена
Код:
[12:28:54] <= Response: 01 03 1C FF C8 01 D5 02 CB 02 38 00 01 00 01 00 01 00 00 00 00 00 01 00 00 00 01 00 36 00 47 AA 24 
[12:28:53] => Poll: 01 03 00 00 00 0E C4 0E 
[12:28:50] Recv error: Exception Response:
The device responded but with an error instead of data

0x02 - ILLEGAL DATA ADDRESS

The data address sent in the query is not an allowable address for the server (or slave). More specifically, the combination of reference number and transfer length is invalid. For a controller with 100 registers, a request with offset 96 and length 4 would succeed, a request with offset 96 and length 5 will generate exception 02. A request for offset 200 will also produce this exception.
[12:28:49] <= Response: 01 83 02 C0 F1 
[12:28:48] => Poll: 01 03 00 18 00 02 44 0C 
[12:28:38] Recv error: Exception Response:
The device responded but with an error instead of data

0x02 - ILLEGAL DATA ADDRESS

The data address sent in the query is not an allowable address for the server (or slave). More specifically, the combination of reference number and transfer length is invalid. For a controller with 100 registers, a request with offset 96 and length 4 would succeed, a request with offset 96 and length 5 will generate exception 02. A request for offset 200 will also produce this exception.
[12:28:37] <= Response: 01 83 02 C0 F1 
[12:28:36] => Poll: 01 03 00 18 00 01 04 0D 
[12:28:22] Error - Modbus message invalid data length
[12:28:22] <= Response: 01 03 00 20 F0 
[12:28:21] => Poll: 01 03 00 18 00 00 C5 CD 
[12:28:02] Recv error: Exception Response:
The device responded but with an error instead of data

0x02 - ILLEGAL DATA ADDRESS

The data address sent in the query is not an allowable address for the server (or slave). More specifically, the combination of reference number and transfer length is invalid. For a controller with 100 registers, a request with offset 96 and length 4 would succeed, a request with offset 96 and length 5 will generate exception 02. A request for offset 200 will also produce this exception.
[12:28:00] <= Response: 01 83 02 C0 F1 
[12:28:00] => Poll: 01 03 00 17 00 01 34 0E 
[12:27:48] Recv error: Exception Response:
The device responded but with an error instead of data

0x02 - ILLEGAL DATA ADDRESS

The data address sent in the query is not an allowable address for the server (or slave). More specifically, the combination of reference number and transfer length is invalid. For a controller with 100 registers, a request with offset 96 and length 4 would succeed, a request with offset 96 and length 5 will generate exception 02. A request for offset 200 will also produce this exception.
[12:27:47] <= Response: 01 83 02 C0 F1 
[12:27:46] => Poll: 01 03 00 16 00 01 65 CE 
[12:27:36] Recv error: Exception Response:
The device responded but with an error instead of data

0x02 - ILLEGAL DATA ADDRESS

The data address sent in the query is not an allowable address for the server (or slave). More specifically, the combination of reference number and transfer length is invalid. For a controller with 100 registers, a request with offset 96 and length 4 would succeed, a request with offset 96 and length 5 will generate exception 02. A request for offset 200 will also produce this exception.
[12:27:33] <= Response: 01 83 02 C0 F1 
[12:27:32] => Poll: 01 03 00 15 00 01 95 CE 
[12:27:23] Recv error: Exception Response:
The device responded but with an error instead of data

0x02 - ILLEGAL DATA ADDRESS

The data address sent in the query is not an allowable address for the server (or slave). More specifically, the combination of reference number and transfer length is invalid. For a controller with 100 registers, a request with offset 96 and length 4 would succeed, a request with offset 96 and length 5 will generate exception 02. A request for offset 200 will also produce this exception.
[12:27:22] <= Response: 01 83 02 C0 F1 
[12:27:21] => Poll: 01 03 00 13 00 01 75 CF 
[12:27:02] Recv error: Exception Response:
The device responded but with an error instead of data

0x02 - ILLEGAL DATA ADDRESS

The data address sent in the query is not an allowable address for the server (or slave). More specifically, the combination of reference number and transfer length is invalid. For a controller with 100 registers, a request with offset 96 and length 4 would succeed, a request with offset 96 and length 5 will generate exception 02. A request for offset 200 will also produce this exception.
[12:27:00] <= Response: 01 83 02 C0 F1 
[12:27:00] => Poll: 01 03 00 11 00 01 D4 0F 
[12:26:47] <= Response: 01 03 02 00 01 79 84 
[12:26:46] => Poll: 01 03 00 10 00 01 85 CF 
[12:26:37] <= Response: 01 03 02 00 00 B8 44 
[12:26:37] => Poll: 01 03 00 0F 00 01 B4 09 
[12:26:26] <= Response: 01 03 02 00 00 B8 44 
[12:26:25] => Poll: 01 03 00 0E 00 01 E5 C9 
[12:26:14] <= Response: 01 03 02 00 47 F8 76 
[12:26:14] => Poll: 01 03 00 0D 00 01 15 C9 
[12:26:00] Error - Modbus message invalid data length
[12:26:00] <= Response: 01 03 00 20 F0 
[12:25:59] => Poll: 01 03 00 0D 00 00 D4 09 
[12:25:57] Error - Modbus message invalid data length
[12:25:57] <= Response: 01 03 00 20 F0 
[12:25:56] => Poll: 01 03 00 0D 00 00 D4 09 
[12:25:44] Error - Modbus message invalid data length
[12:25:43] <= Response: 01 03 00 20 F0 
[12:25:43] => Poll: 01 03 00 11 00 00 15 CF 
[12:25:39] Error - Modbus message invalid data length
[12:25:39] <= Response: 01 03 00 20 F0 
[12:25:38] => Poll: 01 03 00 11 00 00 15 CF 
[12:25:10] Recv error: Exception Response:
The device responded but with an error instead of data

0x02 - ILLEGAL DATA ADDRESS

The data address sent in the query is not an allowable address for the server (or slave). More specifically, the combination of reference number and transfer length is invalid. For a controller with 100 registers, a request with offset 96 and length 4 would succeed, a request with offset 96 and length 5 will generate exception 02. A request for offset 200 will also produce this exception.
[12:25:09] <= Response: 01 83 02 C0 F1 
[12:25:08] => Poll: 01 03 00 14 00 01 C4 0E 
[12:24:57] Recv error: Exception Response:
The device responded but with an error instead of data

0x01 - ILLEGAL FUNCTION

The function code received in the query is not an allowable action for the server (or slave). This may be because the function code is only applicable to newer devices, and was not implemented in the unit selected. It could also indicate that the server (or slave) is in the wrong state to process a request of this type, for example because it is unconfigured and is being asked to return register values. 
[12:24:56] <= Response: 01 81 01 81 90 
[12:24:55] => Poll: 01 01 00 14 00 01 BD CE 
[12:24:45] Recv error: Exception Response:
The device responded but with an error instead of data

0x01 - ILLEGAL FUNCTION

The function code received in the query is not an allowable action for the server (or slave). This may be because the function code is only applicable to newer devices, and was not implemented in the unit selected. It could also indicate that the server (or slave) is in the wrong state to process a request of this type, for example because it is unconfigured and is being asked to return register values. 
[12:24:43] <= Response: 01 82 01 81 60 
[12:24:43] => Poll: 01 02 00 14 00 01 F9 CE 
[12:24:30] Recv error: Exception Response:
The device responded but with an error instead of data

0x01 - ILLEGAL FUNCTION

The function code received in the query is not an allowable action for the server (or slave). This may be because the function code is only applicable to newer devices, and was not implemented in the unit selected. It could also indicate that the server (or slave) is in the wrong state to process a request of this type, for example because it is unconfigured and is being asked to return register values. 
[12:24:26] <= Response: 01 84 01 82 C0 
[12:24:25] => Poll: 01 04 00 14 00 01 71 CE 
[12:22:45] Recv error: Exception Response:
The device responded but with an error instead of data

0x02 - ILLEGAL DATA ADDRESS

The data address sent in the query is not an allowable address for the server (or slave). More specifically, the combination of reference number and transfer length is invalid. For a controller with 100 registers, a request with offset 96 and length 4 would succeed, a request with offset 96 and length 5 will generate exception 02. A request for offset 200 will also produce this exception.
[12:22:43] <= Response: 01 83 02 C0 F1 
[12:22:43] => Poll: 01 03 00 14 00 01 C4 0E 
[12:22:41] <= Response: 01 03 02 00 00 B8 44 
[12:22:40] => Poll: 01 03 00 0F 00 01 B4 09 
[12:22:31] Error - Modbus message invalid data length
[12:22:31] <= Response: 01 03 00 20 F0 
[12:22:31] => Poll: 01 03 00 63 00 00 B5 D4 
[12:22:27] Error - Modbus message invalid data length
[12:22:27] <= Response: 01 03 00 20 F0 
[12:22:26] => Poll: 01 03 00 63 00 00 B5 D4 
[12:22:23] <= Response: 01 03 02 00 00 B8 44 
[12:22:22] => Poll: 01 03 00 0F 00 01 B4 09 
[12:22:20] Recv error: Exception Response:
The device responded but with an error instead of data

0x02 - ILLEGAL DATA ADDRESS

The data address sent in the query is not an allowable address for the server (or slave). More specifically, the combination of reference number and transfer length is invalid. For a controller with 100 registers, a request with offset 96 and length 4 would succeed, a request with offset 96 and length 5 will generate exception 02. A request for offset 200 will also produce this exception.
[12:22:18] <= Response: 01 83 02 C0 F1 
[12:22:17] => Poll: 01 03 00 14 00 01 C4 0E 
[12:22:15] Recv error: Exception Response:
The device responded but with an error instead of data

0x03 - ILLEGAL DATA VALUE

A value contained in the query data field is not an allowable value for server (or slave). This indicates a fault in the structure of the remainder of a complex request, such as that the implied length is incorrect. It specifically does NOT mean that a data item submitted for storage in a register has a value outside the expectation of the application program, since the MODBUS protocol is unaware of the significance of any particular value of any particular register. 
[12:22:12] <= Response: 01 83 03 01 31 
[12:22:12] => Poll: 01 03 00 10 00 02 C5 CE 
[12:21:52] <= Response: 01 03 1C FF C6 01 CD 02 C6 02 3B 00 01 00 01 00 01 00 00 00 00 00 01 00 00 00 01 00 36 00 48 41 9C 
[12:21:51] => Poll: 01 03 00 00 00 0E C4 0E 
[11:42:00] Recv error: Exception Response:
The device responded but with an error instead of data

0x02 - ILLEGAL DATA ADDRESS

The data address sent in the query is not an allowable address for the server (or slave). More specifically, the combination of reference number and transfer length is invalid. For a controller with 100 registers, a request with offset 96 and length 4 would succeed, a request with offset 96 and length 5 will generate exception 02. A request for offset 200 will also produce this exception.
[11:41:57] <= Response: 01 83 02 C0 F1 
[11:41:56] => Poll: 01 03 00 14 00 01 C4 0E 
[11:41:44] Recv error: Exception Response:
The device responded but with an error instead of data

0x02 - ILLEGAL DATA ADDRESS

The data address sent in the query is not an allowable address for the server (or slave). More specifically, the combination of reference number and transfer length is invalid. For a controller with 100 registers, a request with offset 96 and length 4 would succeed, a request with offset 96 and length 5 will generate exception 02. A request for offset 200 will also produce this exception.
[11:41:42] <= Response: 01 83 02 C0 F1 
[11:41:41] => Poll: 01 03 00 13 00 01 75 CF 
[11:41:32] Recv error: Exception Response:
The device responded but with an error instead of data

0x02 - ILLEGAL DATA ADDRESS

The data address sent in the query is not an allowable address for the server (or slave). More specifically, the combination of reference number and transfer length is invalid. For a controller with 100 registers, a request with offset 96 and length 4 would succeed, a request with offset 96 and length 5 will generate exception 02. A request for offset 200 will also produce this exception.
[11:41:30] <= Response: 01 83 02 C0 F1 
[11:41:29] => Poll: 01 03 00 13 00 08 B5 C9 
[11:41:27] <= Response: 01 03 02 00 00 B8 44 
[11:41:26] => Poll: 01 03 00 0F 00 01 B4 09 
[11:41:25] Error - Modbus message invalid data length
[11:41:25] <= Response: 01 03 00 20 F0 
[11:41:24] => Poll: 01 03 00 63 00 00 B5 D4 
[11:41:15] Error - Modbus message invalid data length
[11:41:15] <= Response: 01 03 00 20 F0 
[11:41:14] => Poll: 01 03 00 63 00 00 B5 D4 
[11:41:11] <= Response: 01 03 02 00 00 B8 44 
[11:41:10] => Poll: 01 03 00 0F 00 01 B4 09 
[11:40:56] Recv error: Exception Response:
The device responded but with an error instead of data

0x02 - ILLEGAL DATA ADDRESS

The data address sent in the query is not an allowable address for the server (or slave). More specifically, the combination of reference number and transfer length is invalid. For a controller with 100 registers, a request with offset 96 and length 4 would succeed, a request with offset 96 and length 5 will generate exception 02. A request for offset 200 will also produce this exception.
[11:40:54] <= Response: 01 83 02 C0 F1 
[11:40:54] => Poll: 01 03 00 13 00 08 B5 C9 
[11:40:52] Recv error: Exception Response:
The device responded but with an error instead of data

0x02 - ILLEGAL DATA ADDRESS

The data address sent in the query is not an allowable address for the server (or slave). More specifically, the combination of reference number and transfer length is invalid. For a controller with 100 registers, a request with offset 96 and length 4 would succeed, a request with offset 96 and length 5 will generate exception 02. A request for offset 200 will also produce this exception.
[11:40:50] <= Response: 01 83 02 C0 F1 
[11:40:49] => Poll: 01 03 00 13 00 08 B5 C9 
[11:40:48] Recv error: Exception Response:
The device responded but with an error instead of data

0x03 - ILLEGAL DATA VALUE

A value contained in the query data field is not an allowable value for server (or slave). This indicates a fault in the structure of the remainder of a complex request, such as that the implied length is incorrect. It specifically does NOT mean that a data item submitted for storage in a register has a value outside the expectation of the application program, since the MODBUS protocol is unaware of the significance of any particular value of any particular register. 
[11:40:45] <= Response: 01 83 03 01 31 
[11:40:45] => Poll: 01 03 00 10 00 02 C5 CE 
[11:40:43] <= Response: 01 03 1C FF C0 01 DC 02 DA 02 48 00 01 00 01 00 01 00 00 00 00 00 01 00 00 00 01 00 36 00 49 51 A3 
[11:40:43] => Poll: 01 03 00 00 00 0E C4 0E 
[11:30:27] <= Response: 01 03 20 FF C0 01 DE 02 DF 02 40 00 01 00 01 00 01 00 00 00 00 00 01 00 00 00 01 00 36 00 49 00 00 00 00 5A 97 
[11:30:26] => Poll: 01 03 00 00 00 10 44 06 
[11:30:11] Recv error: Exception Response:
The device responded but with an error instead of data

0x03 - ILLEGAL DATA VALUE

A value contained in the query data field is not an allowable value for server (or slave). This indicates a fault in the structure of the remainder of a complex request, such as that the implied length is incorrect. It specifically does NOT mean that a data item submitted for storage in a register has a value outside the expectation of the application program, since the MODBUS protocol is unaware of the significance of any particular value of any particular register. 
[11:30:09] <= Response: 01 83 03 01 31 
[11:30:09] => Poll: 01 03 00 00 00 12 C5 C7 
[11:29:18] <= Response: 01 03 22 FF BF 01 DF 02 DE 02 43 00 01 00 01 00 01 00 00 00 00 00 01 00 00 00 01 00 36 00 49 00 00 00 00 00 01 94 DA 
[11:29:17] => Poll: 01 03 00 00 00 11 85 C6 
[11:29:06] Recv error: Exception Response:
The device responded but with an error instead of data

0x03 - ILLEGAL DATA VALUE

A value contained in the query data field is not an allowable value for server (or slave). This indicates a fault in the structure of the remainder of a complex request, such as that the implied length is incorrect. It specifically does NOT mean that a data item submitted for storage in a register has a value outside the expectation of the application program, since the MODBUS protocol is unaware of the significance of any particular value of any particular register. 
[11:29:05] <= Response: 01 83 03 01 31 
[11:29:04] => Poll: 01 03 00 00 00 12 C5 C7 
[11:28:53] <= Response: 01 03 20 FF BF 01 E0 02 DD 02 44 00 01 00 01 00 01 00 00 00 00 00 01 00 00 00 01 00 36 00 49 00 00 00 00 01 21 
[11:28:52] => Poll: 01 03 00 00 00 10 44 06 
[11:28:37] <= Response: 01 03 1C FF BF 01 E0 02 DE 02 42 00 01 00 01 00 01 00 00 00 00 00 01 00 00 00 01 00 36 00 49 36 FE 
[11:28:37] => Poll: 01 03 00 00 00 0E C4 0E 
[11:28:28] <= Response: 01 03 18 FF BF 01 E0 02 E0 02 3F 00 01 00 01 00 01 00 00 00 00 00 01 00 00 00 01 71 9F 
[11:28:27] => Poll: 01 03 00 00 00 0C 45 CF 
[11:28:18] <= Response: 01 03 16 FF BF 01 E0 02 E0 02 3D 00 01 00 01 00 01 00 00 00 00 00 01 00 00 F1 B8 
[11:28:17] => Poll: 01 03 00 00 00 0B 04 0D 
[11:27:23] <= Response: 01 03 14 FF BF 01 E0 02 DB 02 4B 00 01 00 01 00 01 00 00 00 00 00 01 AF 66 
[11:27:22] => Poll: 01 03 00 00 00 0A C5 CD 
[11:27:10] Recv error: Exception Response:
The device responded but with an error instead of data

0x03 - ILLEGAL DATA VALUE

A value contained in the query data field is not an allowable value for server (or slave). This indicates a fault in the structure of the remainder of a complex request, such as that the implied length is incorrect. It specifically does NOT mean that a data item submitted for storage in a register has a value outside the expectation of the application program, since the MODBUS protocol is unaware of the significance of any particular value of any particular register. 
[11:27:09] <= Response: 01 83 03 01 31 
[11:27:08] => Poll: 01 03 00 00 00 14 45 C5 
[11:26:59] Recv error: Exception Response:
The device responded but with an error instead of data

0x03 - ILLEGAL DATA VALUE

A value contained in the query data field is not an allowable value for server (or slave). This indicates a fault in the structure of the remainder of a complex request, such as that the implied length is incorrect. It specifically does NOT mean that a data item submitted for storage in a register has a value outside the expectation of the application program, since the MODBUS protocol is unaware of the significance of any particular value of any particular register. 
[11:26:58] <= Response: 01 83 03 01 31 
[11:26:57] => Poll: 01 03 00 00 00 1A C4 01 
[11:26:41] Recv error: Exception Response:
The device responded but with an error instead of data

0x03 - ILLEGAL DATA VALUE

A value contained in the query data field is not an allowable value for server (or slave). This indicates a fault in the structure of the remainder of a complex request, such as that the implied length is incorrect. It specifically does NOT mean that a data item submitted for storage in a register has a value outside the expectation of the application program, since the MODBUS protocol is unaware of the significance of any particular value of any particular register. 
[11:26:40] <= Response: 01 83 03 01 31 
[11:26:40] => Poll: 01 03 00 00 00 1B 05 C1 
[11:26:30] Recv error: Exception Response:
The device responded but with an error instead of data

0x03 - ILLEGAL DATA VALUE

A value contained in the query data field is not an allowable value for server (or slave). This indicates a fault in the structure of the remainder of a complex request, such as that the implied length is incorrect. It specifically does NOT mean that a data item submitted for storage in a register has a value outside the expectation of the application program, since the MODBUS protocol is unaware of the significance of any particular value of any particular register. 
[11:26:29] <= Response: 01 83 03 01 31 
[11:26:28] => Poll: 01 03 00 00 00 1E C5 C2 
[11:26:08] <= Response: 01 03 14 FF BE 01 E1 02 DD 02 45 00 01 00 01 00 01 00 00 00 00 00 01 53 86 
[11:26:07] => Poll: 01 03 00 00 00 0A C5 CD 
[11:25:56] Recv error: Exception Response:
The device responded but with an error instead of data

0x03 - ILLEGAL DATA VALUE

A value contained in the query data field is not an allowable value for server (or slave). This indicates a fault in the structure of the remainder of a complex request, such as that the implied length is incorrect. It specifically does NOT mean that a data item submitted for storage in a register has a value outside the expectation of the application program, since the MODBUS protocol is unaware of the significance of any particular value of any particular register. 
[11:25:54] <= Response: 01 83 03 01 31 
[11:25:53] => Poll: 01 03 00 00 00 64 44 21 
[11:25:53] Connect to COM 11:9600,N,8,1.0 timeout: 3
[11:23:27] Disconnected
[11:19:59] Recv error: Exception Response:
The device responded but with an error instead of data

0x01 - ILLEGAL FUNCTION

The function code received in the query is not an allowable action for the server (or slave). This may be because the function code is only applicable to newer devices, and was not implemented in the unit selected. It could also indicate that the server (or slave) is in the wrong state to process a request of this type, for example because it is unconfigured and is being asked to return register values. 
[11:19:42] <= Response: 01 84 01 82 C0 
[11:19:42] => Poll: 01 04 00 00 00 64 F1 E1 
[11:19:26] Recv error: Exception Response:
The device responded but with an error instead of data

0x03 - ILLEGAL DATA VALUE

A value contained in the query data field is not an allowable value for server (or slave). This indicates a fault in the structure of the remainder of a complex request, such as that the implied length is incorrect. It specifically does NOT mean that a data item submitted for storage in a register has a value outside the expectation of the application program, since the MODBUS protocol is unaware of the significance of any particular value of any particular register. 
[11:19:08] <= Response: 01 83 03 01 31 
[11:19:08] => Poll: 01 03 00 00 00 64 44 21 
[11:18:57] Recv error: Exception Response:
The device responded but with an error instead of data

0x01 - ILLEGAL FUNCTION

The function code received in the query is not an allowable action for the server (or slave). This may be because the function code is only applicable to newer devices, and was not implemented in the unit selected. It could also indicate that the server (or slave) is in the wrong state to process a request of this type, for example because it is unconfigured and is being asked to return register values. 
[11:18:32] <= Response: 01 82 01 81 60 
[11:18:32] => Poll: 01 02 00 00 00 64 79 E1 
[11:18:18] Recv error: Exception Response:
The device responded but with an error instead of data

0x01 - ILLEGAL FUNCTION

The function code received in the query is not an allowable action for the server (or slave). This may be because the function code is only applicable to newer devices, and was not implemented in the unit selected. It could also indicate that the server (or slave) is in the wrong state to process a request of this type, for example because it is unconfigured and is being asked to return register values. 
[11:17:51] <= Response: 01 81 01 81 90 
[11:17:51] => Poll: 01 01 00 00 00 64 3D E1 
[11:17:49] Recv error: Exception Response:
The device responded but with an error instead of data

0x01 - ILLEGAL FUNCTION

The function code received in the query is not an allowable action for the server (or slave). This may be because the function code is only applicable to newer devices, and was not implemented in the unit selected. It could also indicate that the server (or slave) is in the wrong state to process a request of this type, for example because it is unconfigured and is being asked to return register values. 
[11:17:47] <= Response: 01 81 01 81 90 
[11:17:47] => Poll: 01 01 00 00 00 64 3D E1 
[11:17:29] Recv error: Exception Response:
The device responded but with an error instead of data

0x03 - ILLEGAL DATA VALUE

A value contained in the query data field is not an allowable value for server (or slave). This indicates a fault in the structure of the remainder of a complex request, such as that the implied length is incorrect. It specifically does NOT mean that a data item submitted for storage in a register has a value outside the expectation of the application program, since the MODBUS protocol is unaware of the significance of any particular value of any particular register. 
[11:17:27] <= Response: 01 83 03 01 31 
[11:17:27] => Poll: 01 03 00 00 00 64 44 21 
[11:17:05] Recv error: Exception Response:
The device responded but with an error instead of data

0x03 - ILLEGAL DATA VALUE

A value contained in the query data field is not an allowable value for server (or slave). This indicates a fault in the structure of the remainder of a complex request, such as that the implied length is incorrect. It specifically does NOT mean that a data item submitted for storage in a register has a value outside the expectation of the application program, since the MODBUS protocol is unaware of the significance of any particular value of any particular register. 
[11:16:56] <= Response: 01 83 03 01 31 
[11:16:56] => Poll: 01 03 00 00 00 64 44 21 
[11:16:56] Connect to COM 11:9600,N,8,1.0 timeout: 3
[11:10:08] Ready...
[11:10:06] Settings file:  [C:\Users\Lord\Documents\CAS Modbus Scanner\Settings.xml]
[11:10:06] Debug file:  [C:\Users\Lord\Documents\CAS Modbus Scanner\Debuglog.txt]
[11:10:06] Starting up...


__________________
C уважением, LordN